I'm interested in what you decide on because I plan to include a backup gen system in a remodel. I'm also on propane and plan to use that for the generator because it has big storage, doesn't deteriorate, and has lower engine maintenance. I have a 5K Honda gen but it isn't set up for automatic.
I know a fellow in Ned who sells and services GE whole house generators, but I haven't studied the options.
https://gensizer.assurancepower.com/...ouse&Itemid=55
A Load calculator for generator sizing. I put some numbers in quick. Figured on a 3 ton Ac. Came out as 22kw. To meet code with an automatic transfer switch for the whole house you either need to size generator to load calc or rent a power logger for 30 days to see what your peak kw was. I don't know if you power company can give you that information or not.
Screenshot of sample load calc.
Attachment 76160
NEC 220.87
Quote:
220.87 Determining Existing Loads. The calculation of a feeder or service load for existing installations shall
be permitted to use actual maximum demand to determine the existing load under all of the following
conditions:
(1) The maximum demand data is available for a 1-year period.
Exception: If the maximum demand data for a 1-year period is not available, the calculated load shall
be permitted to be based on the maximum demand (measure of average power demand over a 15-
minute period) continuously recorded over a minimum 30-day period using a recording ammeter or
power meter connected to the highest loaded phase of the feeder or service, based on the initial
loading at the start of the recording. The recording shall reflect the maximum demand of the feeder or
service by being taken when the building or space is occupied and shall include by measurement or
calculation the larger of the heating or cooling equipment load, and other loads that may be periodic in
nature due to seasonal or similar conditions.
(2) The maximum demand at 125 percent plus the new load does not exceed the ampacity of the feeder or
rating of the service.
(3) The feeder has overcurrent protection in accordance with 240.4, and the service has overload
protection in accordance with 230.90.
NEC 702.4
Quote:
(B) System Capacity. The calculated load on the standby source must
be in accordance with Article 220 or by another method approved by
the authority having jurisdiction.
(1) Manual Transfer Equipment. The optional standby power source
must have adequate capacity for all equipment intended to operate at
one time as determined by the user.
Author’s Comment:
n When a manual transfer switch is used, the user of the
optional standby system selects the loads to be connected to
the system, which determines the system kVA/kW rating.
(2) Automatic Transfer Equipment.
(a) Full Load. The optional standby power source must have adequate
capacity to supply the full load transferred.
I disagree that any extended use with propane would be much different from gasoline or diesel. Call your propane supplier and ask their experts what they think. I went with propane primarily because it is so much cleaner. Gasoline in storage for long periods degrades and additives increase the cost so that needs to be considered as well. Then all commercial generators made for gasoline will specify non-ethanol fuel. Very expensive. Now diesel could be a good choice but see how easy it can be had in your area using farm or non highway use fuel. About a 40 cent per gallon savings.
Sent from my iPhone using Tapatalk
I had a whole home one and I had 400 amp service for the home because I had a large home and lots of electricity being used in it. I had a Generac and transfer switch that could handle the whole load and never had an issue with it. Would do its weekly self test and come on by itself which was comforting to hear. Ran on propane out in the country north and east of Kiowa so I know what you are saying about not wanting to count on the electric always being there.