    Have a head scratcher.
    Building an electric brew kettle using a 5500 watt hot water heating element.

    Built a subpanel and control box that plugs into my dryer outlet. Using a 50 amp gfci spa panel for some don't electrocute myself protection. With a potentiometer controlled solid state relay to control the power into the element.



    anyway
    fired it up 2 nights ago and ran some water up to a boil everything worked perfectly.

    Fast forward to today and I plugged it in and it tripped the breaker immediately. Not the breaker in the main panel but just my gfci. Ohmed out everything have no continuity where it shouldn't be all connections right and tight

    I then disconnected all wiring on the outlet side of the breaker and it still trips. Measured 2 hot legs at the wall plug and getting 124.6 and 126.1 volts. Same volt reading on both the ground and neutral.


    Is that voltage difference enough to trip the breaker? Any other ideas as to what could be causing the issue?
    You sir, are a specialist in the art of discovering a welcoming outcome of a particular situation....not a mechanic.

    My feedback add 11-12 ish before the great servpocaylpse of 2012

  2. #2
    Grand Master Know It All
    Join Date
    Mar 2006
    Location
    Dickshooter, ID
    Posts
    4,828

    Default

    Check for broken neutral or ground

  3. #3
    If I had a son he would look like....Ben SideShow Bob's Avatar
    Join Date
    Mar 2010
    Location
    SE Aurora
    Posts
    7,120

    Default

    Did you wire it in properly ? Recheck & retighten all connections, if it worked once, a loose connection at the curly neutral to the neutral bus is likely the problem.
    Click image for larger version. 

Name:	image.jpeg 
Views:	40 
Size:	120.0 KB 
ID:	64336
    Last edited by SideShow Bob; 03-08-2016 at 17:58.
    My T.P. wheeling and dealing feedback is here.

    Opinions are like assholes, everybody has one, and it stinks more than mine.


    Yo Homie, That my chainsaw ?



    Pati, improbe et vince

  4. #4
    Beer Meister DFBrews's Avatar
    Join Date
    Dec 2010
    Location
    With the classyish Hipsters...Stapleton
    Posts
    3,175

    Default

    Quote Originally Posted by SideShow Bob View Post
    Did you wire it in properly ? Recheck & retighten all connections, if it worked once, a loose connection at the curly neutral to the neutral bus is likely the problem.
    Click image for larger version. 

Name:	image.jpeg 
Views:	40 
Size:	120.0 KB 
ID:	64336
    Click image for larger version. 

Name:	image.jpg 
Views:	55 
Size:	248.9 KB 
ID:	64337
    Triple checked all connections. Line in is all tight. Not using the neutral on the element side so it is terminated.
    You sir, are a specialist in the art of discovering a welcoming outcome of a particular situation....not a mechanic.

    My feedback add 11-12 ish before the great servpocaylpse of 2012

  5. #5
    If I had a son he would look like....Ben SideShow Bob's Avatar
    Join Date
    Mar 2010
    Location
    SE Aurora
    Posts
    7,120

    Default

    That is your problem. The load side neutral does not go to the neutral bus. ( From the load side of the breaker.)
    Also, if that is a GFCI breaker, it looks like it is missing the curled neutral that should go to the neutral bus. ( See the lower left of the illustration, it appears more of a zig zag.)
    Last edited by SideShow Bob; 03-08-2016 at 18:22.
    My T.P. wheeling and dealing feedback is here.

    Opinions are like assholes, everybody has one, and it stinks more than mine.


    Yo Homie, That my chainsaw ?



    Pati, improbe et vince

  6. #6
    Beer Meister DFBrews's Avatar
    Join Date
    Dec 2010
    Location
    With the classyish Hipsters...Stapleton
    Posts
    3,175

    Default

    Quote Originally Posted by SideShow Bob View Post
    That is your problem. The load side neutral does not go to the neutral bus. ( From the load side of the breaker.)
    Also, if that is a GFCI breaker, it looks like it is missing the curled neutral that should go to the neutral bus. ( See the lower left of the illustration, it appears more of a zig zag.)
    the load side neutral is not being used at all. And the curled wire on the breaker Is stretched to make it to the neutral bus
    You sir, are a specialist in the art of discovering a welcoming outcome of a particular situation....not a mechanic.

    My feedback add 11-12 ish before the great servpocaylpse of 2012

  7. #7
    Paper Hunter
    Join Date
    Nov 2008
    Location
    Olympic peninsula of Washington
    Posts
    255

    Default

    Looks to me that he has the load side neutral capped off at the bottom of the panel. I believe the wire he has going to the neutral buss is the "curled" wire. Might just be a bad GFI breaker.

  8. #8
    Beer Meister DFBrews's Avatar
    Join Date
    Dec 2010
    Location
    With the classyish Hipsters...Stapleton
    Posts
    3,175

    Default

    Quote Originally Posted by laportecharlie View Post
    Looks to me that he has the load side neutral capped off at the bottom of the panel. I believe the wire he has going to the neutral buss is the "curled" wire. Might just be a bad GFI breaker.
    correct Charlie

    have an an email into Home Depot see if they will swap out just the breaker or if I have to take everything apart and send them the entire panel
    You sir, are a specialist in the art of discovering a welcoming outcome of a particular situation....not a mechanic.

    My feedback add 11-12 ish before the great servpocaylpse of 2012

  9. #9
    Beer Meister DFBrews's Avatar
    Join Date
    Dec 2010
    Location
    With the classyish Hipsters...Stapleton
    Posts
    3,175

    Default

    Click image for larger version. 

Name:	image.jpg 
Views:	24 
Size:	246.0 KB 
ID:	64338Here's my diagram like I said I can take the load side completely out and it still trips. If I pull the curly white from the neutral bus it does not trip
    You sir, are a specialist in the art of discovering a welcoming outcome of a particular situation....not a mechanic.

    My feedback add 11-12 ish before the great servpocaylpse of 2012

  10. #10
    Beer Meister DFBrews's Avatar
    Join Date
    Dec 2010
    Location
    With the classyish Hipsters...Stapleton
    Posts
    3,175

    Default

    Now I'm confused!

    My wiring in the first picture is
    red and black hot leg go into their respective slots into the breaker
    line in green ground goes to ground bus
    white neutral goes to neutral bus
    curly wire from gfci goes into neutral bus.

    This set up with nothing on the load side still trips the breaker immediately.
    Going to buy another breaker (at 100 bucks a pop ouch) and see if the problem continues.
    You sir, are a specialist in the art of discovering a welcoming outcome of a particular situation....not a mechanic.