    Quote Originally Posted by Colorado Fatboy View Post
    Are you sure the ground and neutral are not bonded in the box? Lift all ground and neutral wires then check continuity between ground and neutral bars.

    Edit to add: In the pic it appears there is a screw or something o right side of neutral bar touching can? Hard to tell for sure from pic.

    Isolated and ohmed during initial troubleshooting no continuity anywhere it shouldn't be. And the gold screw top right of the sub panel is not touching the box itself it is isolated with a piece of plastic and is what holds the neutral bar to the box itself on a piece of plastic


    kinda want to put it on a different 240 circuit and see if the problem follows meaning I have a problem on my dryer circuit but sadly my stove has a different plug.