12.5 amps so I think you need at least 12 ga, maybe more depending on how far it is.
12.5 amps so I think you need at least 12 ga, maybe more depending on how far it is.
The calculation for that load (12.5 amps) & distance (120 ft.) works out to 10 AWG, for a 3% loss...
Be sure to get the UF (gray, underground DB rated), not the white non- DB rated Romex.