    12.5 amps so I think you need at least 12 ga, maybe more depending on how far it is.

  2. #2
    If I had a son he would look like....Ben SideShow Bob's Avatar
    Join Date
    Mar 2010
    Location
    SE Aurora
    Posts
    7,120

    Default

    The calculation for that load (12.5 amps) & distance (120 ft.) works out to 10 AWG, for a 3% loss...

    Be sure to get the UF (gray, underground DB rated), not the white non- DB rated Romex.
    Last edited by SideShow Bob; 10-20-2016 at 19:04.