    Default Lead acid battery exploded

    Went to check our backup generator before the incoming storm. No cranking love. Look things over and find that the starter battery has literally exploded. Blew the top cap off and cracked the case on one side. I can fill 5 out of the 6 cells. It did this once before a year ago, blowing the cap off but didn't crack the case. I refilled and recharged, everything seemed back to normal.

    I checked it this spring when I did an oil change. Battery is dated 11/2013. This is the first battery I've had in decades that requires checking fluid levels. Seems odd for an emergency appliance. Part #51 72J, 625 cranking amps, if that means anything.

    Would welcome advice on either a much better battery or what I need to do better. Don't think this storm will be an issue but I want to be ready for the next one.

  2. #2
    Zombie Slayer
    Join Date
    Sep 2009
    Location
    Pueblo
    Posts
    6,910

    Default

    Water evaporated and the electrolyte became too acidic. That caused flowering of the plates and battery case cracked. Batteries are usually only good for 5 years. Batteries Plus or a similar store should be able to find you a replacement. A sealed gel cell should fit and be of more cold cranking amps (CCA) than a typical lead acid battery.

  3. #3
    Machine Gunner
    Join Date
    Sep 2011
    Location
    westminster
    Posts
    2,228

    Default

    Agm battery would be my choice.

  4. #4
    Machine Gunner
    Join Date
    Jan 2007
    Location
    Longmont, CO
    Posts
    2,180

    Default

    Where is the bat located? Does it see extreme heat and cold?

  5. #5
    OtterbatHellcat
    Join Date
    Feb 2013
    Location
    Central Arizona
    Posts
    21,941

    Default

    Hensley is a good place to get batteries.


    ΜΟΛ
    ΩΝ ΛΑΒΕ

    My Feedback

  6. #6
    Varmiteer
    Join Date
    Mar 2013
    Location
    Westish of Boulder
    Posts
    559

    Default

    Thanks guys, I'll probably get an AGM for replacement.

    Erni, the generator is outside so battery sees same temps as a vehicle with far less vibration. Rarely gets below 0°F anymore and seldom above 93°F.

  7. #7
    If I had a son he would look like....Ben SideShow Bob's Avatar
    Join Date
    Mar 2010
    Location
    SE Aurora
    Posts
    7,120

    Default

    I had an old 1963 Chevy pick up converted to an alternator, I didn’t do the conversion correctly. It would over charge the battery causing the fluid to boil, in turn causing excessive out gassing (hydrogen & oxygen) and a sparking which caused the battery to actually explode violently.
    This happened twice before I figured out the problem.

    If you get an acidic sulfury smell when the generator isrunning, or see misty gases venting from the battery, shut down the generator and check the charging system.
    Last edited by SideShow Bob; 01-21-2018 at 10:50.
    My T.P. wheeling and dealing feedback is here.

    Opinions are like assholes, everybody has one, and it stinks more than mine.


    Yo Homie, That my chainsaw ?



    Pati, improbe et vince

  8. #8
    Gong Shooter
    Join Date
    May 2013
    Location
    DENVER, CO
    Posts
    399

    Default

    What maintains voltage on this battery?

    I would recommend quality Deka brand no maintenance type, bet you it lasts a very long time (5+ yr easy) if you have it on a quality maintainer ("battery tender jr" would do it)

  9. #9
    Gong Shooter
    Join Date
    May 2013
    Location
    DENVER, CO
    Posts
    399

    Default

    Quote Originally Posted by SideShow Bob View Post
    I had an old 1963 Chevy pick up converted to an alternator, I didn’t do the conversion correctly. It would over charge the battery causing the fluid to boil, in turn causing excessive out gassing (hydrogen & oxygen) and a sparking which caused the battery to actually explode violently.
    This happened twice before I figured out the problem.

    If you get an acidic sulfury smell when the generator isrunning, or see misty gases venting from the battery, shut down the generator and check the charging system.
    Very good point here as there is likely a separate charging system for maintenance and one that runs with the gens motor.

  10. #10
    Gong Shooter
    Join Date
    May 2006
    Location
    Castle Rock
    Posts
    301

    Default

    This is why all building emergency generators have a quality battery maintainer and a battery heater. Cold will kill a battery.