  1. #11
    Recognized as needing a lap dance
    Join Date
    Jan 2010
    Location
    SW Missouri
    Posts
    5,540

    Default

    Quote Originally Posted by SideShow Bob View Post
    Sorry Kev, you will have to increase wire size and over current devises for this circuit
    If you want to run a welder and heater on the same branch circuit. And you will have to install a sub panel to service both.

    You will be able to run either or, but not both.
    But one or the other should be fine? And putting that heater on a plug would eliminate attempting to use both as you mentioned before?

  2. #12
    If I had a son he would look like....Ben SideShow Bob's Avatar
    Join Date
    Mar 2010
    Location
    SE Aurora
    Posts
    7,120

    Default

    The plug is not manufacturer installed, also the heater is a permanently installed unit.
    If the heater was manufactured with wheels or a stand and a cord with plug you would be OK and could utilize it that way as a portable unit.

    Now, if you so chose, as the home owner and accept all liability, to install a plug & cord onto the heater. Or chose to hardwire the heater in and leave the plug usable and relied on your common sense to not use both at the same time.......Let?s just say I have seen worse home owner wiring jobs.

    I cannot condone or advise you on doing the above mentioned methods, what you do in the privacy of your own garage is your business.....

    Now pay your bill, or I will start a thread and out you as a dead beat !
    Last edited by SideShow Bob; 11-24-2018 at 18:55.
    My T.P. wheeling and dealing feedback is here.

    Opinions are like assholes, everybody has one, and it stinks more than mine.


    Yo Homie, That my chainsaw ?



    Pati, improbe et vince

  3. #13
    Recognized as needing a lap dance
    Join Date
    Jan 2010
    Location
    SW Missouri
    Posts
    5,540

    Default

    Quote Originally Posted by SideShow Bob View Post
    The plug is not manufacturer installed, also the heater is a permanently installed unit.
    If the heater was manufactured with wheels or a stand and a cord with plug you would be OK and could utilize it that way as a portable unit.

    Now, if you so chose, as the home owner and accept all liability, to install a plug & cord onto the heater. Or chose to hardwire the heater in and leave the plug usable and relied on your common sense to not use both at the same time.......Let?s just say I have seen worse home owner wiring jobs.

    I cannot condone or advise you on doing the above mentioned methods, what you do in the privacy of your own garage is your business.....

    Now pay your bill, or I will start a thread and out you as a dead beat !
    Ok I appreciate your guidance to follow the law as closely as possible.

  4. #14
    Grand Master Know It All BladesNBarrels's Avatar
    Join Date
    Oct 2010
    Location
    Lakewood, CO
    Posts
    3,636

    Default

    Do you have room in your electrical panel for another 220 circuit for the heater?
    And, is the panel rated for another circuit?

    I am not an electrician and I do not play one on TV

    Buying Randall Made Knives and Randall 1911 Pistols

    BladesNBarrels Feedback

  5. #15
    Industry Partner BPTactical's Avatar
    Join Date
    Dec 2009
    Location
    North Metro
    Posts
    13,900

    Default

    Quote Originally Posted by SideShow Bob View Post
    The plug is not manufacturer installed, also the heater is a permanently installed unit.
    If the heater was manufactured with wheels or a stand and a cord with plug you would be OK and could utilize it that way as a portable unit.

    Now, if you so chose, as the home owner and accept all liability, to install a plug & cord onto the heater. Or chose to hardwire the heater in and leave the plug usable and relied on your common sense to not use both at the same time.......Let?s just say I have seen worse home owner wiring jobs.

    I cannot condone or advise you on doing the above mentioned methods, what you do in the privacy of your own garage is your business.....

    Now pay your bill, or I will start a thread and out you as a dead beat !


    Yo Homie, is that my Hubble plug?
    The most important thing to be learned from those who demand "Equality For All" is that all are not equal...

    Gun Control - seeking a Hardware solution for a Software problem...

  6. #16
    Gong Shooter
    Join Date
    May 2006
    Location
    Castle Rock
    Posts
    301

    Default

    Quote Originally Posted by SideShow Bob View Post
    The plug is not manufacturer installed, also the heater is a permanently installed unit.
    If the heater was manufactured with wheels or a stand and a cord with plug you would be OK and could utilize it that way as a portable unit.

    Now, if you so chose, as the home owner and accept all liability, to install a plug & cord onto the heater. Or chose to hardwire the heater in and leave the plug usable and relied on your common sense to not use both at the same time.......Let?s just say I have seen worse home owner wiring jobs.

    I cannot condone or advise you on doing the above mentioned methods, what you do in the privacy of your own garage is your business.....

    Now pay your bill, or I will start a thread and out you as a dead beat !
    This is the correct answer. Your overcurrent/Overload protection is correct and the rest is up to you to do the right things with both the welder and heater.
    S&W M&P-15T, XD40 Tac.,& XD40 Subcompact, Springfield 1911 RO and Mil spec, 870 turkey, Benelli SBEII, Rem 750.
    Listen to my scanner feed here. http://www.radioreference.com/apps/audio/?feedId=46